MPPT RS 450/100 off during sunny day, error code 27 during power up

I've 3 MPPT RS 450/100 which I installed 2 weeks ago. One of them had a problem during firmware update using Victron Connect and Bluetooth. Further updates in Victron Connect weren't possible because the device always reported firmware up2date (1.09).

But after startup of the Cerbo GX this device reported an error on the MPPT RS, error code 117, incompatible firmware error. Then I was able to update the firmware again and this time successfully, it seems.


And this device stopped working, produced no energy today. It was off most of the time.

Bildschirmfoto 2022-05-11 um 00.25.24.png

In the evening I switched off the device. After powering it up again the Cerbo GX reported an error 27, Charger short circuit until I heared a clicking in the MPPT RS device.

Bildschirmfoto 2022-05-11 um 00.27.55.png

Is the device faulty, or any suggestions what to do?

Thanks

MPPT Controllers
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

6 Answers
pripp avatar image
pripp answered ·

Here is the same problem.
After the FW update to V1.09 the MPPT 450/100 the error 27 shows up.
This always happens during low load conditions in the morning or evening. (See time)

Victron please fix the firmware.


error27.png


error27.png (59.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pripp avatar image
pripp answered ·

Even with firmware v1.10 the problem persists.

victron-error27.png


victron-error27.png (178.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

petajoule avatar image
petajoule answered ·

How are the PV panels connected in both cases?
Because if you had some parallel setup per string and the (double, triple,...) short circuit currents of the PV modules exceed the MPPT specification you could see this error.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pripp avatar image
pripp answered ·

No parallel strings.
String module short current (10,8A < 18A) is below max. rating of the MPPT.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

petajoule avatar image petajoule commented ·
Well, I experience this error too maybe once every 4-5 weeks, also under low light conditions. Device operating well otherwise.

This happened with 1.10, I just updated to 1.11, we'll see if the frequency of these #27 errors increases or decreases.


0 Likes 0 ·
petajoule avatar image petajoule petajoule commented ·
No issue since 1.11 - *knocks on wood*.
0 Likes 0 ·
bartholdl avatar image
bartholdl answered ·

I have the same problem with my RS 450/100, with firmware 1.10. In the morning, in very low light conditions (200W or so total input), I get the charger short circuit #27 error. Doesn't happen every morning, but several times a week. Firmware bug, or a real issue?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

bartholdl avatar image
bartholdl answered ·

Here's another example of what looks like an incorrect datapoint? How can the 450/100 be in both bulk and off state at the same time? Look at the two datapoints around 14:00. If it is just a logging glitch that is one thing. But if this reset the absorption timer, for example, back to zero, that would not be good for my batteries. Anyone any idea?