There were some discussions on battery capacity evaluations but they did not really answer my question/concerns.
I have 16 CALB Lifepo4 prismatic cells 400Ah connected in series to get 48v. So, nominal capacity is about 20kWh. Battery is 7 years old (time flies!). Batteries promised 2000 cycles for 80% DD. This is a good manufacturer and their batteries were tested before to deliver this promise. 2000 cycles is about 7 years. But I never went that far down. My typical DD 25-49%, not more. So, I should expect some life in the battery
I want to expand my total storage capacity. I try to evaluate remaining capacity to understand: is it worth to add a similar battery pack in parallel or I need to build a new system with new batteries.
All methods with "charge to 100% and then discharge to 50% or 20%" don't work for me. They are impractical. I live off-grid from this battery charging from solar. I need energy for the house, and charging is not up to me - it depends on sun. It is not so easy to discharge 10-16kWh in one go, and if I do it then there is a chance I might not be able to charge it back as there is no sun.
Hence, the only way for me is a natural experiment and observations.
I assume that Multi derives SOC based on the voltage, and Multi knows that I use Lifepo4 battery. So, if I collect SOC and consumption numbers from VRM portal, I might be able to get some idea of the remaining capacity.
For example, SOC after sunset s1 = 98.5% and consumption so far is c1 = 4.9kWh. Then I check the same parameters next day before sunrise, s2 = 66% and c2 = (7.61+3.48) = 11.09kWh as there are two days.
Estimated capacity should be (c2 - c1) / (s2 - s1) = (11.09 - 4.9) / (0.985 - 0.66) = 19.0kWh
I tried this approach several times for different SOCs and time periods and I got numbers around 19kWh. If SOC is low or time interval is short, then estimation might be lower, e.g. 18kWh. Sometimes it is higher, e.g. 20kWh. But most time it is very close to 19kWh.
Could you please comment on this approach and reliability of my estimation?
19kWh looks good, it might make sense just to add another 16 cells in parallel and use them for the next 7 years.