What change do I need to do to see Bulk/absorption/float status on Vrm instead of Ext. Control?

Greetings everyone,

What change do I need to do to see Bulk/absorption/float status on Vrm instead of Ext. Control that I have constantly now (see attachments)?


screenshot-from-2022-05-05-11-03-25.png



screenshot-from-2022-05-05-11-03-39.png

The little but of float is because I just connected the MPPT to the Cerbo yesterday.


Thank you

VRM
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi @Michaeltenerife,

In an "externally controlled" system, the built in charge algorithms are disabled. So Bulk, Abs, and float algorithms are no longer used.

This is most often done when a system charge state is being managed by an external lithium battery BMS for example.

There is a little bit more about it in the manual here.


7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

michaeltenerife avatar image michaeltenerife commented ·
E

ohh, ok. So if understand it well: because I connected my pylontech battery to the cerbo as well, the battery is controlling automatically the mppt? There is no need for configuration here anymore? From Victron advice for pylontech batterie charging configuration (https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom) the following information was given: screenshot-from-2022-05-05-11-34-43.pngEven though I introduced these values in the MPPT configuration, this is now overwritten by the battery for it's optimum care. Is that so?


Thank you for confirming.

0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ michaeltenerife commented ·

For the most part, yes, more or less :)

Following the installation instructions as written in that Pylontech battery compatibility guide is exactly the right thing to do. They have been applied to 1000's of reliable systems over many years.

0 Likes 0 ·
Show more comments
Peter Chambers avatar image Peter Chambers commented ·

Thanks for clarifying. It would be useful for the display on the Touch screen to show the charge decision that the BMS decides. The LEDs on the Quattro show Bulk, Absorption, etc even while the screen displays Ext.Control. The Touch screen used to show the charging mode in previous firmware revisions (before last Autumn).

0 Likes 0 ·
derrick thomas avatar image derrick thomas Peter Chambers commented ·

In a system with a managed battery the led status is meaningless. Regardless of what the LEDs are indicating, the CV and CC are being controlled by the BMS.

1 Like 1 ·