question

Alex Black avatar image
Alex Black asked

Smart shunt - battery percentage is incorrect, how to calibrate

I have a smart shunt with a fairly old agm battery (unknown as to its condition).

I have fully charged the battery to float 13.2v using a victron smart charger. At that point, on the shunt I set state of charge to 100%

The battery is currently at 12.6v after overnight use and the shunt is reporting 98%. According to https://www.energymatters.com.au/battery-voltage-discharge/ at that voltage it should be around 75%. I have no doubt that this old battery has deteriorated, but is there a way to configure the shunt to show a more “true” charge level?

I also note that the agm is a 260 ah 12v. I’ve read that this shouldn’t be discharged below 50%, on the shunt settings should I enter into “battery capacity” 260 or 130ah?

SmartShunt
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
snoobler avatar image
snoobler answered ·

13.2V is nowhere near fully charged. AGM batteries are typically charged to 14.2-14.8V, held there for 2+ hours until current drop to 0.01-0.03C (0.02C = 5.2A in your case) and then floated at 13.4-13.8V. The actual numbers depend on the manufacturer.


Beware of trusting resting voltage to SoC charts. It is not consistent across manufacturers. It's also not accurate if the battery has been charged or discharged within the last several hours. 12.6V is pretty meaningless as a measure of state of charge based on your description. In other words, resting voltage to SoC is only accurate after the battery has sat passing no current for at least two hours. Depending on manufacturer and type, the most accurate relationship is after resting a full 24 hours.


Concerning 50% discharge, yes. All lead-acid batteries should be discharged no more than 50% in most cases. Discharges down to 20% are typically safe, but they will reduce cycle life. Again, this depends on manufacturer and battery type. No, you should not enter 50% as your total capacity. There may come times where you may need to go a little below 50% rather than lose a critical function, e.g., shutting down your RV propane furnace when it's really cold outside. Maybe you'll be okay with the occasional dip down to 20-30% SoC rather than freeze your butt off. If you enter an artificially low capacity, your SoC will be wrong below 50%... when it matters most.


What you do instead is set your discharge floor to 50%. The "time remaining" value uses total capacity and this % to compute your time remaining.



2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·
@Alex Black

I'd just add that tired AGM batteries will often come up to charged voltage very quickly and once 'charged' you'll see them run out of power just as quickly.

A fully charged AGM will drop to around 12.6V without any significant loss of charge. Your 12.6V/98% value can be considered correct.

You can set alarms based on SOC, high/low voltage in the smart shunt.

0 Likes 0 ·
Show more comments
Alex Black avatar image
Alex Black answered ·

Thank you for your replies. Over the last 6 or so days it’s been quite cloudy so the solar hasn’t had a chance to charge the batteries, below are some screenshots of the battery status. The RV is in the driveway so there’s no use (TVs, lights, etc) over the last 7 days.

Draw is about 0.8amp at rest (modem, raspberry pi Venus OS, some small draw electronics).

It reads 90.6% at 12.28v, which seems a high % for that voltage. All websites I look at say at around 12.3v it should be at 70% charge.

Any thoughts on the stats below?

https://imgur.com/a/rOn57kD




2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

snoobler avatar image
snoobler answered ·

Even the small 0.8A draw is going to pull your battery voltage lower than resting voltage. You are likely > 70% SoC. Voltage vs. SoC is only truly accurate after the battery has been completely disconnected (no charge or discharge of any kind) for several hours.

If you really want to estimate SoC, completely disconnect the battery from any loads or charging for about 8 hours.

Accuracy of the shunt is improved with periodic charges to full with a 100% sync. It's probably a little high, but it's more about potential degradation of the battery vs. rated capacity.

This video shows how to properly configure a BMV-700 series unit, which is essentially identical to the smartshunt:

https://www.youtube.com/watch?v=4ReljfO3k6M

How much solar do you have?

Please include snapshots of your smartshunt and solar charge controller settings.

IMHO, if you can't get your batteries charged daily, you need a new solution. Recommend floating them at 13.8V via an AC powered charger or whatever your manufacturer recommends. This will get them fully charged.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alex Black avatar image
Alex Black answered ·

Here’s screenshots of the battery setup and consumption screen https://imgur.com/a/NllRkOk

There’s 240w of solar but it’s partially obstructed by the Maxxair fan. Planning to address solar when I do a off grid upgrade eventually. I’ll review that video on setting up the shunt correctly.

I do have a shore charger for the leisure batteries, I’ll hook it up. Thanks for your help

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·
Your charged voltage is very low, despite that the battery isn't getting charged enough to get the shunt to resynchronize. @snoobler suggestion of external charger will resolve part of this, but charged voltage needs to go up to about 14.4V, otherwise you'll get a false synch.
0 Likes 0 ·
snoobler avatar image
snoobler answered ·

Per the instructions in that video, you need to set your charged voltage to 0.2V below your SOLAR bulk/boost/absorption voltage.


Shade, even partial, DESTROYS solar output. Depending on panel construction, shading even ONE cell in panel will cut its output by as much as 33%.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.