Zero feed-in problem

We have a problem with the EM24 and the zero feed in the ESS. The screenshot shows that supposedly 0 kWh has been fed in.
1651478581191.png


In fact, however, 6 kWh were fed in.

1651478703228.png

1651478790194.png



1651478875778.png

The system has the following components:

1651479561926.png

We use the original Victron cable for data transmission. V2.85 is used on a rpi.

We have set the mains supply to 500W on a trial basis. However, this does not prevent the grid feed-in either!

Where could the error lie?

em24
1651478581191.png (55.0 KiB)
1651478703228.png (46.0 KiB)
1651478790194.png (22.4 KiB)
1651478875778.png (33.3 KiB)
1651479561926.png (33.4 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
marekp avatar image
marekp answered ·

@MaHa

Try changing "multiphase regulation" from "total of all phases"

screen-shot-2022-05-02-at-10445-pm.png

to "individual phase"

screen-shot-2022-05-02-at-10546-pm.png



2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

maha avatar image
maha answered ·

We replaced the multi with another one and everything works fine with it. This means that the first Multi is working incorrectly. I'm curious to see how the repair will go...

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic

Energy Meter Manual EM24 RS485