Victron Mega Fuse slow blown issues

A 100 amp Victron Mega fuse blowns at 250amp accroding to this video (289) Testing 100A Fuses with 100A of current. - YouTube

I am concern then how to choose the correct fuse for a 100a wire capacity, a 60amp?

fuses
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
sebastianlehmann avatar image
sebastianlehmann answered ·

Victron Fuse Test

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

We had this topic a few months ago with the same video.
Unfortunately I can't find that topic right now.

A 100A fuse should be able to carry 100A for a infinite time, it should not blow at 100A.
I guess he first fuse and that breaker tested in that video will also blow at 90A or less if that current runs for a while and ambient temperature is a bit higher.
The guy in the video is rising the current to fast, he should go up in 5A steps and let it run for 5-10 minutes.
It is also written in some comments below that video.