I have Multiplus 2 in a 3 phase system, an AC coupled old Solar and 2 DC coupled MPPTs.
Running ESS with a 28 KWh Pylontech 48V Battery.
The old solar can feed the excess energy to the grid.
The new Victron system is not allowed to the grid and is a so called “Zero Feed in” system (“Nulleinspeisung” in German).
When my Battery reaches 95%, the charge current will be throttled like it should be.
Currently first all local Victron MPPTs reduce the power down till 0W. But the Adsorption and Float Loading continue using the loading device of the Multiplus 2.
I want to revert this locic, because my Solar system is allowed to feed to the grid, the Victron system not. So first the Multiplus Charger shall throttle and go down to 0, and second the MPPTs. Is this possible?