I have a client having a multiplus low voltage warning coming on regulary and also a allarm warning triggering ,
So the question is - is anyone else seeing this low voltage warning light happening ?????? and is wondering why. ??????
now the clients LiPO bank is in the final stages of balancing as I have 6 cells at 3.50 to 3.52v and two cells at 3.34v so the BMS is telling the multiplus and the smartsolar mppt to STOP charging as it should and I suspect by reducing the ccl to zero - and at this point I suspect that a INCORRECT low battery voltage warning is occurring.
Hardware installed 1 x Multiplus 24/3000, 1 x 150/35 MPPT 1 x 123smart BMS 8 x calb se200 cells 1 x Cerbo on fw 2.85
---------------------------------------------------------
1. multiplus on Newest fw 496 (No assistants installed)
2. I am thinking its occuring when the BMS changes the CCL to zero amps that this light then comes on
3. the alarm log is showing heaps of these warnings
4. DVCC is turned on and no assistants have been installed.