Small BMS, Charge & Load disconnects for multiple devices.

Hello,

I’m seeking some advice or direction regarding load and charge disconnecting multiple devices from a Small BMS.

Curent setup,

160ah smart lithium, Small BMS, Orion Smart dc converter 2x 12-12-30, Smart mppt 75-15, victron smart inverter 2000va, smart batter protect 65.


In it’s current configuration, the SBP is connected to the vans load and controlled directly from the BMS’s load Disconnect

One of the onions is directly controlled by the BMS’s charge disconnect

My first question is how do I control the 2nd Orion, and the mppt in the event of under or over temperature? Can I simply daisy chains the charge disconnect from the BMS to all chargers? if not what’s best practice?

my second question is how do I disconnect the inverters load directly from the BMS? Or will this need an additional battery protect?

it seems like there are many scenarios to load and charge disconnect but not many outputs from the bms?


Thank you in advance


BMS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

@T3Z-GB

Not daisy chain them but wire them up to a distributor and from there with one wire into charge disconnect of your smallBMS.

For the MPPT you'll need a VE.Direct non inverting remote on/off cable that goes to the same distributor.

For the MultiPlus I think the 2-signal BMS assistant is required or alternatively a VE.Bus BMS. I suggest you search the forum for that one. I'm not experienced with that. A BatteryProtect with your Multi is no good idea because there's a risk of reverse current which will destroy the BatteryProtect.

Hope that helps.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

t3z-gb avatar image t3z-gb commented ·

@Stefanie

I don’t understand what you mean, everything is connected to a lynx Distributor, how would I turn both Orions and the mppt off with just one charge disconnect on the BMS.

Regarding the inverter I have just the Victron smart inverter 2000va not a multiplus.


Thanks.

0 Likes 0 ·