This is on a Large 34 Mtr boat thats at a marina most of the time and at other times out on charter.
Now The part I am having issues is as the AC1 in (and we can export power but very unlikey that this would occur) (country set to OTHER) and setting up the assistant works fine so that the solar power is use first and the grid supplements this as needed.
Self consumption Hub 1, Connected to the Mains no feed back (requires a country code Other used)
The issue is that when the Generator starts (AC1 in disconnected) then when it trys to Sync and connect its immediately disconnected due to a LOM issue . (it did show the error but I did not take a photo) anyway is there a way to stop this LOM issue I did try o disable this but it needed a password, so I could not do it to set if that would work.
Basically we dont need to export any solar to the grid, we just want to use all the DC connected solar and then supply the balance of the power from the GEN or the Shore Power when connected. the Marina charges stupid fees for there power so we want to use a little as possible (like 5 times normal domestic prices)
Any other better solutions for setup or advise are welcome
setup as below and all works well
2 x Quattro 24/8000 units FW 433 in Parralle
1 x CCGX Fw 2.23
1 x BMV 712
2 x Smart Solar 250/85 MPPT Regulators
20kw Lithium Battery bank
We have main Grid power connected to AC1 in
We have Onon 18Kw Generator connected to AC2 in with Autostart connected to the CCGX
We have connected AC1 out to the Boat (AC2 is not used)
the Solar regs are connected directly to the Batteries