Smartsolar 150/70 showing incorrect battery voltage after v3.07 firmware update

I have a very strange problem. I have a smartsolar 150/70 that is showing a battery voltage approximately 3v higher after the firmware was updated to v3.07. I have checked the voltage at the terminals on the unit and it is the same as the batteries. It was reading fine on the previous firmware. So, for example, if the battery voltage is 48v, the charger is reading 51v. This is causing it to float and stop charging way too soon. I have swapped the unit with a 150/35 with the latest firmware and the voltage reads fine. It seems to just be the 150/70 unit that has the problem. I would understand if it was reading lower that there could have potentially been a wiring problem or something like that, but it was suddenly reading higher and only with this unit. Has anyone else noticed this problem?

MPPT Controllersvoltage
17 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ads-eng avatar image ads-eng commented ·
Same problem on MPPT 250/100

Battery voltage on app shows 59 V actual battery voltage 54.6 V

Charger is not charging battery nor feeding back to the grid

0 Likes 0 ·
jaspar avatar image jaspar ads-eng commented ·
Thanks for your response. I expect there will be lots of people that don't realise they have this problem, because they never check the voltage on the batteries vs what the app says. I'm hoping someone from Victron support can do some tests and confirm this is an issue with the current firmware.
0 Likes 0 ·
nickdb avatar image nickdb ♦♦ commented ·
There seems to be a 3.10 available.
0 Likes 0 ·
offroadflow avatar image offroadflow nickdb ♦♦ commented ·
solved?
0 Likes 0 ·
jaspar avatar image jaspar offroadflow commented ·

Victronconnect on my android is saying my 150/70 firmware is up to date at v3.07. Is there a link I can manually download v3.10 or do I have to wait until it is pushed out to me?

0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ jaspar commented ·
0 Likes 0 ·
offroadflow avatar image offroadflow klim8skeptic ♦ commented ·
He isn't asking for the VC software, but the firmware for the MPPT...
0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ offroadflow commented ·
Click on the link?
0 Likes 0 ·
offroadflow avatar image offroadflow klim8skeptic ♦ commented ·
...and?

Same thing.

Asked for: FIRMWARE for the MPPT

Answered with:

SOFTWARE VictronConnect

Regards

0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ offroadflow commented ·
The firmware is in the software.
0 Likes 0 ·
jaspar avatar image jaspar klim8skeptic ♦ commented ·
I've installed v3.10 but it doesn't fix the problem.
0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ jaspar commented ·
Bump.


You dont have any voltage compensation enabled?

0 Likes 0 ·
Show more comments
offroadflow avatar image offroadflow klim8skeptic ♦ commented ·
?

Since when?

The software is the program managing the update.

The firmware is downloaded indivudually.

0 Likes 0 ·
nickdb avatar image nickdb ♦♦ offroadflow commented ·
Firmware is embedded into victron connect for local updating.
0 Likes 0 ·
Show more comments
1 Answer
Paul B avatar image
Paul B answered ·

Download the older firmware onto a your phone or tablet or computer and then update it manually back to the older version that you had originally. and retest it then, if it continues then take it back to a Victron agent for testing

https://professional.victronenergy.com/downloads/firmware/

1652596546275.png


1652596546275.png (61.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic

MPPT Product Page

MPPT Error codes

MPPT 150/60 up to 250/70 Manual