question

guy-planner avatar image
guy-planner asked

Input vs Output question

Input vs Output question; I am connecting my Victron’s 100/50 MPPT onto 4x 200W 24V solar panels (panels are rated max 37.6V & 5.36A). Panels will be connected in parallel, therefore max MPPT input would be 21.4A under perfect conditions.

Q; I am worried the MPPT’s output current may be in excess of 50A. eg. if input current ever reaches 21A, at 37V, does it mean the output current at 12.5 volts would be 62A ? (WAV rule, watts=amps x volts)

MPPT Controllers
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

The controller will limit the output to 50A.
At 14.8V battery Voltage then you will be harvesting 740W from your panels. Your system is quite well dimensioned.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

guy-planner avatar image guy-planner commented ·
that is a relief, thank you for your input :)