Can MP-II's AC-out-2 be programmed to have power when grid fails?

I found this in MP-II documentation:

Auxiliary AC output (AC-out-2)
Intended for non-critical loads. Default behaviour only allows AC-out-2 after a 30 second delay when AC input is detected. A Current measurement circuit enables PowerAssist. Override programming for more control of this relay is possible.

Where I can find something about this "override programming"?

ac-out-2
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

You have to use the "programmable relay" assistant.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
Yes, mine stays on until 70% SOC then switches off. So you can have it quite flexible.
0 Likes 0 ·
marekp avatar image marekp Alexandra ♦ commented ·

@Matthias Lange - DE

@Alexandra

Thank you both for this info. I suspected that this "programmable relay" has interesting features but documentation on it is scarce.