question

nostromo avatar image
nostromo asked

No current or power limit in scheduled charge mode

Does anyone know how to explain the setting of current or power in programmed charging mode ? Apparently there is no current or power limit.

powerassist
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

@nostromo

The charge and current limit will be whatever the battery requires or asks the system for, limited by the input current limit and battery charging profile programmed into the grid tab of the inverter.

Or in some cases altered by the DVCC settings by the user.

Also each inverter has its own max current charging ability to the battery bank.

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nostromo avatar image nostromo commented ·

@ Alexandra, I'll check again if limit is taken into account in sheduled programming mode.

0 Likes 0 ·
Show more comments
nostromo avatar image
nostromo answered ·

@ Alexandra

Solution is to limit the input current limit of the inverter. No sexy solution, would be preferable to have a setting as per power limit as from the solar charger.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic