I asked this question previously .
We have Lifepo4 battery and the boat 12v load is via a smart battery protect. I set this to Li-ion mode but we don’t have a Victron BMS. The inverter is a Quattro 5000. All this is connected to a Cerbo GX and the remote for the SBP has its remote off connected to an REC-ABMS. The problem we have is that if the BMS shuts down the system it also shuts off the SBP. When we start the generator it comes on but the Quattro doesn’t go to charge mode, I am sure this is because the Cerbo GX isn’t powered up because it’s power comes from the boat 12v system which because the SBP has been turned off by the BMS doesn’t restart and thereafter tell the Quattro to resume charging ? Any ideas ?
Update
It was suggested that I power the Cerbo GX direct from the Battery at the Quattro input but this is at odds with the Victron advice found in various places that says.
Never power the GX device directly from the battery as it can keep consuming power after the the battery has reached its low voltage threshold. This will further discharge the battery and can cause damage to the battery.
So the question remains if the Quattro won’t come back to charge mode without the Cerbo GX being powered up, where would I connect the Cerbo GX power supply ?
For now we just turn off the Quattro and then restart, at which point it goes to charge mode and within a few seconds the SBP comes back on as the REC-ABMS tells the remote to switch on and the Cerbo GX powers up and keeps the Quattro running in charge mode.
Once we have solar this probably won’t happen so often but currently we regularly get the BMS shutting down the Quattro and SBP early in the morning so when we get up everything is off so we start the dinosaur squeezing converting machine to restore battery power.