I have 8 trojan T-105 in series on a bluesolar MPPT 150/70.
trojan T-105 lead acid data sheet
from what I can read there is that the manufacturer calls for 0.005V or 5mV per cell temperature compensation. I have 24 cells.
victron bluesolar MPPT 150/70 manual
the manufacturer calls for the following voltages:
Absorption: 59.28V
Float: 54.00V
Equalisation: 64.80V
I have set my charger (page 11 in the manual) to option 8 (USR).
But the maximum compensation voltage (option 20 on page 15 of the manual) only allows for -3.5mV which is 0.0035V.
Unfortunately I had just fried over 4 years a set of 24 trojan T-105 because of not optimum settings. now i am trying to correct that error with my new set of 8.
my charger is running firmware version 2.04
is there a newer firmware that allows for the required correct compensation temperature for the tojan T-105 (0.005V per cell) to be set?