lynx smart bms discharge floor adjustment

Hi

I have a mobile system with a lynx smart bms and cerbo gx that is monitored in real time.

Is it possible to raise or lower the discharge floor on a lynx smart bms and if so is it possible via cerbo gx on VRM

Thanks Grant

BMS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

@IandDIndustries

Unfortunately this is not yet possible. Discharge floor is a fixed value (10%) that cannot be changed.

I'm missing this feature too and will forward this to the developers. Maybe they can make this user adjustable.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ianddindustries avatar image ianddindustries commented ·
Hi Stefanie

thanks for the reply

The lynx manual states the discharge floor is set at 15% however my system turned off at 10% as you stated

came up with #36 ATC/ATD failure

consumed amp hours of -578.8

battery 23.17v

Its a 600 amp 24v system if it had turned the ATD off at 15% and not the ATC as well it would of had time to allow the solar to kick in and charge up again?

System was plugged into mains and all is now well

Regards