Hi
I have a mobile system with a lynx smart bms and cerbo gx that is monitored in real time.
Is it possible to raise or lower the discharge floor on a lynx smart bms and if so is it possible via cerbo gx on VRM
Thanks Grant
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi
I have a mobile system with a lynx smart bms and cerbo gx that is monitored in real time.
Is it possible to raise or lower the discharge floor on a lynx smart bms and if so is it possible via cerbo gx on VRM
Thanks Grant
Unfortunately this is not yet possible. Discharge floor is a fixed value (10%) that cannot be changed.
I'm missing this feature too and will forward this to the developers. Maybe they can make this user adjustable.
thanks for the reply
The lynx manual states the discharge floor is set at 15% however my system turned off at 10% as you stated
came up with #36 ATC/ATD failure
consumed amp hours of -578.8
battery 23.17v
Its a 600 amp 24v system if it had turned the ATD off at 15% and not the ATC as well it would of had time to allow the solar to kick in and charge up again?
System was plugged into mains and all is now well
Regards
Grant