Just got our multiplus 24v 3000w 50amp inverter and are getting multiple issues

We live in a Skoolie… System is currently connected to shore power - our system has 110v fridge which pulls 400w per 24hours and 12v lights - couple plugs to charge our phones/iPads - we use way less currently than the system is set up for. But we plan to add a heat/ac in the future.

Inverter is in absorption mode - set to 8 hour time, is that appropriate?

We have 8 -270ah lifePo4 wired in series to create 24v battery

We got a dc ripple alert and the inverter shut off. We turned it back on then off and on again based on the basic troubleshooting.

Our whole system is the Bluetooth connection systems from victron -

It says charged to 100% - 26.6v -

We’ve only had the system up and running for 2 days.

Could really use some insight. Just really confused after two days of it working perfectly.

inverter current drawdc system
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Alexandra avatar image
Alexandra answered ·

@Whiskeywilderness

8hour absorption time is too long for lifepo4. Set it to one hour. The battery bms seems to be unhappy. What are the recommended charge voltages? And are the cells all balanced?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

whiskeywilderness avatar image whiskeywilderness commented ·
Can you elaborate on what you mean by charge voltages? For what part? Battery? Bms?
0 Likes 0 ·
snoobler avatar image
snoobler answered ·

Did you top balance your battery cells before deployment?


What BMS?


LFP requires very little absorption time. The only time you want a long absorption time is if you're trying to restore balance in an unbalanced battery. 1 hour should be sufficient.


If the BMS is triggering high voltage protection due to cell over-volt, I can see the MP reacting with excessive ripple.



2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

whiskeywilderness avatar image whiskeywilderness commented ·

The batteries are all balanced and now the inverter of turning off and on, every 3-4 minutes.

0 Likes 0 ·
snoobler avatar image snoobler whiskeywilderness commented ·
Did you purchase "matched" cells, or did you actually go through the process of top balancing the cells?


What BMS?


What absorption voltage?


What are the cell voltages doing when the MP is cycling on and off.


This sounds like classic cell imbalance and BMS cut-off.

0 Likes 0 ·
Trevor Bird avatar image
Trevor Bird answered ·

@Whiskeywilderness the following may be a plausible story. The internal BMS of the battery may be switching cells in and out creating instability of the terminal voltage. This is misinterpreted by the MP as DC Ripple and it shuts down. This can happen more so for series strings because a BMS does not exist across the entire battery bank, only the individual batteries. Batteries can charge at different rates so voltage imbalance can occur across the batteries and across the individual cells within the batteries. To stop this happening lower the absorption voltage the charger is set to. Lower it by 2 volts to start with and see if the instability improves. Run it like that for a while and if you want to raise the voltage a little but not up to where it was. Cell balancing refers to each cell in the battery having the same voltage. If the internal cell voltage reaches 3.75 volts the BMS disconnects it to stop it overcharging as a protection mechanism. Each 12 volt battery has 4 of those so the BMS tries to keep them all “balanced”

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

whiskeywilderness avatar image whiskeywilderness commented ·
We have a 24v 200a Daly BMS on the batteries.
0 Likes 0 ·
Show more comments
whiskeywilderness avatar image whiskeywilderness commented ·

So we did what you recommended and reduced it by two volts as well as resetting our bms and that seems to have done the trick. Time will tell.