Correct wiring of wireless victron shunt

All the information I have found says that only a single wire from the battery neg. terminal should connect to the battery neg of the shunt. Am I correct to assume then that the neg. wire from a solar controller should only go to the load minus side of the shunt?

SmartShunt
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

@Ksb

It is labelled.

But there should be nothing connected between the shunt and the battery. (Except the connecting cable) Everything else is connected to the load side of the shunt.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Trevor Bird avatar image
Trevor Bird answered ·

@Ksb …..yes, all of the current to and from the battery must flow through the shunt for it to keep track of things. The solar ground must connect to the system side of the shunt and not the battery side.