VRM showing wrong SOC

Hi all

I have got a bit of a problem at the moment - perhaps an expert out there can help me with this issue.

Setup: Smart MPPT-150/30, Multiplus (MP)II - 5KVA, Cerbo GX, DIY Lifpo4 battery pack - 12KWh.

Problem: The SOC on VRM is not showing what it is suppose to be. After grid charging of battery to SOC of 95%. The input AC was then disconnected. The SOC has remained at 95% since.

VRM has been showing SOC 95% irrespective of actual battery voltage. This is then stopping charging of batter from MPPT and also from grid via MPII.

No problem whatsoever running this setup at all - Except until yesterday (09/04/2022 to present time)

Tried:

1) Disconncted and reconnected all - MPII & Battery Pack, MPPT and Cerbo GX - NO change.

2) Rebooting Cerbo GX via Remote Console - NO change.

3) Rebooted MPII and grid connection - NO change,

4) Increase Bulk and Float voltage to that higher than Battery Management System (BMS) - battery charged for a small increment due to the increase in MPPT Bulk & Float voltage - other than that NO change.

5) Applied continuous AC load - Battery voltage reduced due to load but SOC on VRM still showing 95%.

6) Applied AC load to drain battery and for BMS to restart - battery voltage dropped, BMS restarted but SOC still at 95%. As you can see on the screen shots Battery Voltage and SOC is in the same parameter box or window.

7) Checked for latest firmware - currently running latest firmware.

8) Changing Battery Monitor in Remote Console to Automatic and MultiplusII - NO Change.

Any assistance is much appreciated.

Many thanks!

Trung.

Screen shot 1 - SOC at 96% with No AC load. This then prevents the MPPT from charging the batteries (at 52.28V - SOC should about 50% - BMS showing 50.3% - connected directly to lifepo4 battery). At 50.3% - MPPT should kick in with the lower battery voltage and actual SOC.

Screen short 2 - SOC at 96% with AC load - SOC should reduce with AC load but it just stays static. MPPT kick in due to AC load / draw (but it should be charging anyway due to low SOC/Voltage).

vrm1.jpgvrm2.jpg



VRMSOC
vrm1.jpg (146.3 KiB)
vrm2.jpg (156.4 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

That SOC measurement is coming from the MultiPlus if I understand your system correctly.
This measurement from inside the MultiPlus cannot measure current from the MPPT, so charge current from the MPPT will not be counted into the battery.
The SOC reading will not prevent the battery from charging. The MPPT charger and MultiPlus charger charge up to their programmed target Voltages and it's these Voltage limits which slow and stop the charging. If your battery is estimated to be around 50% SOC and it stops charging, then the Voltage limit is probably too low. DIY LiFePO4 battery would probably 3.2V per cell, so maybe 3.5V per cell full charge which would result in an absorb Voltage setting of 56.8V.
52.28V is 3.268V per cell which is nowhere near full.

hen you have multiple charging sources, then a BMV or Smartshunt is absolutely ideal for tracking all energy into and out of the battery and then the SOC estimate will be much more realistic.

10 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Trung avatar image Trung commented ·
Hi Wkirby

Many thanks for your comments and reply to my query/problem.

I haven't changed the upper or lower battery charging parameters for about 11months now - a bit of fiddling when I set up the DIY battery pack initially but, I left it once it was running well. So, it has been running really well for the last 11months. It was only yesterday since things went a bit south and the SOC was stuck at 95%.???

I have tried and disconnect the whole system and then connect everything back for a complete system reconnect - I had hoped when this happened, the MPII voltage reading would be closer to the BMS. However, this never happened.

Since the SOC is at 95%, the MPII is not charging the battery pack either. I have disconnected this completely was well - but NO change,

Apart from charging my batteries up to 95% SOC somehow and then connect everything back together again - so that the SOC is representative of the battery SOC (as measured by the BMS), I am a bit stuck on what to do??

Many thanks again...

0 Likes 0 ·
kevgermany avatar image kevgermany ♦♦ Trung commented ·

As @WKirby said SOC does not affect charging.

With your setup you can ignore SOC.

Try checking your AC in connections/fuses/trips. Also please post the charge settings in the multiplus and MPPT.

Also check your assistants. There's one that can ignore AC input.

0 Likes 0 ·
Show more comments
JohnC avatar image JohnC ♦ Trung commented ·
@TrungT

I would turn the Multi SOC off completely. It's just distracting you.

You mention a Voltage discrepancy between the Multi and the BMS. What about that reported by the mppt? It's possible to arrange a 'system' V with DVCC, but if the BMS can't communicate then it won't be included. But if you have V issues then you really must sort that out as a priority. Especially with Li batts.