Assuming no external AC, multiplus will take full input from the battery/charger system. So yes, power from the panels will be driving the multiplus, supplemented by the battery if needed.
If there is a 230 AC external current, which I have an output load consumption of the multiplus2 and that the batteries are full or goes the current of the panels issued by the MPPT Bluesolar or SmartSolar? Can not we prioritize the energy of the panels for loads of charges before taking energy on the AC external ?
My understanding from previous answers is that if set up correctly the MP will in priority order
In order for this to work without an external meter or current transformer all the loads must be connected to AC-Out
HTH
For prioritization, will the multiplus make the energy differential between the battery and the MPPT Bluesolar or SmartSolar connected sets on the 48 VDC thanks to the VE.Direct?
Ess assistant is what you are looking for, through the GX device you can configure all the features you describe.
If your PV is sufficiently sized your entire AC loads can be supported by solar. fYI the 108W from grid is because we are not allowed to feedback so we are preventing it by drawing some from grid.