Hi Guys, I am hoping someone out there might have some insight on a current Off-Grid system we have installed at a remote location. Here is the system:
4ea 10KVA Quattros (120/240v), 10ea 24V 200amp Victron LFP, VE.Bus BMS, 1000amp Smart 712-BMV, CCGX, 3ea 150/85 MPPTs, 24KW Generator (remote on/off set at 25% SOC)
This system has been upgraded on numerous occasions, and this issue is constant. Note: All software/firmware is up to date.
It seems whenever the batteries discharge to 0% in the event our generator runs out of gas or lack of PV output, the system shuts down. Obviously I expect the system to shut down. However, when mains are present (from genset) the system does not come back online, even after a few hours or days.
When the system is down and PV charges the batteries the CCGX comes online but does not wake up the Quattros. A simple ‘redetect’ on the CCGX sees Quattros and the system as whole comes back online.
Why does the system not come online when mains from the generator are present?
**my theory is the VE.Bus BMS is causing the Quattros to maintain in the ‘off’ state. I notice on other installs when we use the Lynx BMS we do not have this issue. My assumption is because the CCGX is recieving battery data Ve.Can and not Ve.Bus.