Solar-Power too high in VRM?

Hi!

I have 10kWp Solar and 3x Multiplus 2 3000 (3x 2400W constant-power = 7200W).
> But no energy-meter!

In the picture you can see that the MP2 are powering 7359W into the grid/house and 82W are going into the battery = 7441W total.

8389 - 7441 = 948W...where are they? :)

- Power-consumption from the Multiplus itself?
- Measurement deviations because i have no energy-meter?

(CVL was set down here at 54,8V so there wasn´t any bigger current going into the battery)


vrm-pv-power-too-high.jpg


VRM
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
nickdb avatar image
nickdb answered ·

Converting DC to AC has overhead, so you will always see more being produced/used on the DC side - 10 to 15%.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

puitl avatar image
puitl answered ·

Ah ok thank you!

Until now i thought there is only about 70W loss in each Multiplus...but then i have to consider the converting itself too.