Hallo
I would like to add a MultiPlus2 48/3000 to the one I have today so I have one on L1 and one on L2 and space on L3 for one more.
The one I have has serial number.
SN: HQ1933WREV4
How does it fit in with the one I can buy today is mine too old?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hallo
I would like to add a MultiPlus2 48/3000 to the one I have today so I have one on L1 and one on L2 and space on L3 for one more.
The one I have has serial number.
SN: HQ1933WREV4
How does it fit in with the one I can buy today is mine too old?
For both configs all units need to be identical, from the docs:
All units in one system must be the same type and firmware version, this includes same size, system voltage, and feature set. The type is indicated by the first four digits of the firmware version number.
@nickdb For parallel setup, not only type of MP-II, but also HW Revision needs to be the same.
Yes i have read it in the documentation but what are the first four digits of firmware version number in a brand new Multiplus 2?