mihaimicu asked

Multiplus 48/5000/70 instalation on thee phase system

Hi all. Need some help. I have one multiplus 48/5000/70 already installed on L1 with 3 pylontechs 2.4 kwh. I want to install another multiplus on L2 but with another battery type. I mention that the batteries and the second multi is already bought. Need some help with the instalation. Wiring and config. I mention that I have a fronius symo 7 kw on the in side a smart meter Em24 and a Venus gx.

multiplus in parallel
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Ants Kosmos avatar image Ants Kosmos commented ·
2x Multiplus 2 and one battery is right. This is for 2 phase.
0 Likes 0 ·
1 Answer
marekp avatar image
marekp answered ·

@Mihaimicu

If that second MP-II will have its own battery, it will have to be totally separate system from the first MP-II. VE.bus interconnection with the first MP-II will not be possible.

It will have to have its own GX controller.

After grid failure those two MP-II system will not be synchronized.

13 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mihaimicu avatar image mihaimicu commented ·

@MarekP as thinking this will have to be the answer. What about the EM24 smart meter and the fronius symo. How they will work with two GX?

0 Likes 0 ·
marekp avatar image marekp mihaimicu commented ·

@Mihaimicu

If I understand it correctly you have EM24 Carlo Gavazzi meter

https://www.victronenergy.com/live/energy-meters:em24

"Smart Meter" is a Fronius product.

I do not think one EM24 meter can be used by two different GX controllers each running its own ESS assistant. (Someone who knows different could correct me)

I think to run two different ESS assistants you would need two single phase ET112 meters for each phase that have MP-II installed. I could be wrong.

Fronius Symo connected at AC-in would not be affected by two separate MP-II systems but I thing GX controllers should not know about its existence.

0 Likes 0 ·