question

Martin Coetzee avatar image
Martin Coetzee asked

Overload alarm leading to error 17

First time i am getting this in day time, 2 x 5kva parralel. i also got a overload error at the same time. I have lowered the input current on my victrons. It was at peak charging at was getting in just under 6000 watts from my panels. Max watts is 8800.

error
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Paul B avatar image
Paul B answered ·

Another possibility to look at


The length of the Battery cables to EACH unit, They must be the SAME length

just maybe one of the cables is longer and causing a issue.


this is just a thought and something to check

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

willemoud avatar image
willemoud answered ·
I suggest to double check the isolation switches

as they may be causing the problem.


victron-control-circuit-breaker.jpg


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.