question

battery-boy avatar image
battery-boy asked

Multiplus 3 phase Mains & Float LED's flashing

I have a 3 phase system, made up of 3 x Multiplus 48/3000/35. The system will not output or charge battery. The Mains and Float LEDs flash simultaneously.

I've checked the system configured the system using VE.Bus Config.

It is switched as a group. and each individual device shows no error when checked.

There is a mains 3 phase supply present at the inputs which has the correct phase rotation.

There is a 48 volt battery on the DC.

Wiring has been checked point to point, and this all rings through correctly.

What is the error being displayed? And how can it be rectified?

Thanks


Neil

multiplus ve.bus
multiplus-error.mp4 (15.1 MiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Battery_Boy

Do yourself a huge favour and get a GX device for the system.

Otherwise check the Victron toolkit.

9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

battery-boy avatar image battery-boy commented ·
@Alexandra


Victron tool kit hasn't got this particular combination, however it appears to be a combination of the input being rejected and battery issue at best guess.

I agree a GX is the go to piece of kit, however in this particular application unnecessary, and it won't diagnose this issue anyway.

Thanks for your comments, it's good to hear someone's out there.

1 Like 1 ·
Show more comments