Trying to understand some curious charging effects on my 12v system. I have a 600Ah AGM batteries bank (in use 3 years), just upgraded components to Victron: SmartShunt with temperature sensor. Charging from a SmartSolar and MultiPlus with DVCC (shared everything) setup on a Cerbo (using SmartShunt temp), and an Orion Smart just doing its thing. All are set to recommended charge profile and temp compensation (-13mV/*F) from the battery manufacturer.
The issue: When I connect MultiPlus to shore power (15a), it works great, gets my batteries up to float and then storage, things are fine. But if I leave it plugged in on storage or float for a few hours, the batteries heat up bigtime. In float/storage they're taking appropriate minimal charge of ~5a, but still eventually heat up to ~110*F in a ~40*F cabinet.
Due to temp compensation, when engaged the Orion/Solar think it needs to bulk charge the full batteries because the MP is only charging at 12.7v or so. This keeps the batteries hot and the voltage low, so the Orion/Solar will try to bulk the full batteries all day. Turning off all charging overnight and letting the batteries cool down allows all devices to charge properly the following days, but any time my MP charges for a while this happens...
Additionally, the 2 times I've tried to equalize with the MP, the batteries go well over 110*F, fill the van with hydrogen off-gas, and set off my CO detectors.
I know these high temps are bad for the batteries, and I'm worried what they'll do in ~80*F ambient summer temps, if they're overheating in the dead of winter in Colorado...
Does anyone have any idea on a fix for this?