Could someone please clarify why the Quattro manual suggests a 100A breaker on the AC1 input when the math says a 5000VA inverter can't exceed 42A at 120VAC? Thank you.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Could someone please clarify why the Quattro manual suggests a 100A breaker on the AC1 input when the math says a 5000VA inverter can't exceed 42A at 120VAC? Thank you.
Because it can pass through up to 100A.