I have recently noticed an inconsistency between the DC bus voltages reported by the Multi (5kva 230/48) and the battery's BMS (BSL).
On VRM (and the GX BMS tab) I could see the BMS reporting just on 54V but the multi was reporting 54.5V, 0.5V higher.
The MPPT's reported the same, which makes sense as they are using shared data anyway.
I checked connections and fetched the trusty fluke meter. This reported 54.2V at the Multi and 54.1V at the battery terminals, that is what I would expect, yet the inverter is reporting much higher.
Is this an iffy voltage sensor?
I checked again this morning under similar loads and they were all agreeing on the reported voltage, so this somewhat inconsistent.
Any thoughts as to the cause? I have had some unexpected charging behaviour so went looking for reasons why.