control Cyrix or BP with BMV instead of BMS

Hi!
Is it possible to control the disconnect function in Cyrix Li-ct (or Battery Protect) with the relay function in BMV712 (instead of the BMS)?

I would like to use the BMV alarm functionality to disconnect the alternator from the house battery when SOC gets close to 100%.

BMV Battery MonitorBattery ProtectCyrix Battery Combiner
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

Yes you can do this as the BMV relay contacts that are normally N/O you can reverse the relay to be N/C thuis opening on a Alarm

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

astor avatar image astor commented ·

Hi @Paul B

It is possible to control in the same way Cyrix CT via BMV?