loomin asked

Charge Source Priority?

Hey Everyone,


I am in the middle of a van conversion. I've got solar, shore power and alternator for charge sources.

I was curious about how the devices in my charging system decide which source to charge from and if they are smart enough to realize that the system is already being charged by another device already. I don't want to jam too much current into my batteries.


My current setup is:

-200AH (100AHx2) AGM batteries (wired in parallel) max charge current is 60A

-310W Solar Panels

-Victron BMV-712

-Victron SmartSolar MPPT 100/30 Smart

-Victron Orion TR smart 12/12-30 Charger

-Kisae IC-122055 AC Charger/Inverter (55A Charge) - Shore Power

https://www.kisaepower.com/wp-content/uploads/2016/07/Inverter-Charger_datasheet_high_frequency.pdf

-Victron Smart Battery Protect - I was thinking of using this to turn off all DC loads with the push of a button.


Scenario 1: If I am plugged into shore power and the sun comes out and the MPPT decides to start charging at the same time, I could see a very high charge current (80A) with both devices trying to charge at the same time, correct? Or would the MPPT somehow detect the charge voltage of my Inverter/Charger and not start?


Scenario 2:

The van is charging from the MPPT and I decide to go for a drive. I start the engine and the Orion decides to start charging. Technically this scenario wouldn't exceed the max charge amps of the battery but I am just using it as an example.


Am I overthinking this?



MPPT ControllersBMV Battery Monitororion-tr smartBattery Protect
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
JohnC avatar image
JohnC answered ·

Hi @Loomin

Overthinking is for people who care for what they do. Welcome.. :)

An all-Victron (and higher end) setup could do what you want, but the kit you have will communicate only by the charge V it detects. Just sayin. But it's not a big deal.

Please check that 60A max is real. That's 0.3C into 200Ah of batts, and probably impossible to achieve anyway in practice with AGM's, at least for more than seconds/minutes. They'll self-limit, show high (target) V, and the charger(s) will back off.

Scenario 1: Even if you'd just turned on the shore power at sunup, the solar will come on slowly, and by the time it can produce anything useful the batts are partly done, and one/both chargers will back off.

Scenario 2: Same story.

The 60A limit does seem unrealistic though, and in practice would likely never be reached.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

loomin avatar image
loomin answered ·

Hey @JohnC


Thanks for clarifying this for me. The spec sheet for a single battery says max charge current is 30A (but recommended is 10-15A each. Since they are in parallel, max charge current becomes 60A am I right?

I just wanted to make sure I don't melt anything when I get everything connected.


Thanks again!


Chris





1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

adric avatar image
adric answered ·

Hi John,

I have a very similar question to Loomin posted here,

https://community.victronenergy.com/questions/48180/how-to-setup-multiple-chargers-connecting-simultan.html

but I received no answer. I guess I can now use your reply to Loomin as a reference, which is great.

However, it would be great to understand how all the three charging devices could be prioritized via the Victron connect app. Would there be a way to do this?

Also, looking at the Victron Van install link, I cannot make sense of the highlighted in yellow section below.

As it seems that the AC/DC Charger flow could be reaching the Battery Protect Out, which I thought was wrong and could cause the BP to fail and catch fire, by reversing the flow.

Shouldn't the AC/DC Charger be connected on the Input side of the BP, like the MPPT and Starter are?

I would appreciate you feedback on both these questions.

Thank you in advance,

Adri


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

adric avatar image
adric answered ·

Thank you Guy and John for your feedback, it is greatly appreciated. Regards, Adri