Order of connecting these devices to a battery bank (Smartshunt, battery disconect, smart battery protect, fuse))

What would be the correct order of connecting these devices to the battery bank and to which terminal?

+ side: fuse only

- side: disconnect switch, smartshunt, smart batteryprotect ?

SmartShunt
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Alexandra avatar image
Alexandra answered ·

@JJ-O-JJ

Cut off switch goes on the hot (positive) side. Otherwise the electrical current could flow if there was an alternative ground for any reason.

The battery isolator/disconnect switch is normally on the +ve. Fuse first then switch.

If you switch the negative the shunt will loose SOC. So on the -ve shunt then loads (battery protect).

Battery protect is uni directional so put charging sources on the shunt as well.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jj-o-jj avatar image
jj-o-jj answered ·

So

+ side: Fuse, Smart Battery protect, Disconnect switch

- side Shunt

https://www.victronenergy.com/blog/wp-content/uploads/sites/10/2019/01/DS-smartBP220_91312006.jpg ?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jj-o-jj avatar image
jj-o-jj answered ·

Ok. i will not have battery protect in system, BMS should be enough protection.

- side: Battery - >BMS>Smart Shunt>loads

+ side: Battery + >Fuse>Cutoff switch>loads


Is this correct?