question

eliott avatar image
eliott asked

New Victron LFP installation constant switch between bulk and absorption

Hi!


I have a new LFP system with with Quattro 48/5000/70-2x100 and 4*Smart Lfp 25,6 200Ah. What I see when charging is the system only switches to absorption for a short time and immediately back to bulk, never to float. Is this normal or expected? The charger voltages are the default from the Quattro. Thanks

Lithium Battery
1553244997585.png (23.0 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image boekel ♦ commented ·

-are these the only components in the system?

-what did you set in the Quattro settings? (screenshots of VE-configure)

0 Likes 0 ·
4 Answers
mihair avatar image
mihair answered ·

From where are the batteries charged, from grid?

When this behaviour happen, constantly switching from Bulk to Absorption,, are the battery almost full (over 90%SOC) ?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

eliott avatar image eliott commented ·

Yes, almost full, charging from grid, limited to 6A@220V.

I see no alarms online in VRM

0 Likes 0 ·
eliott avatar image
eliott answered ·

Yes, this is how the voltages and current look like.


1553263902153.png (81.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

eliott avatar image
eliott answered ·

Yes, almost full, charging from grid, limited to 6A@220V.

I see no alarms online in VRM

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image
boekel answered ·

-are these the only components in the system?

-what did you set in the Quattro settings? (screenshots of VE-configure)

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

eliott avatar image eliott commented ·

Components: Quattro, CCGX, BMV, VE.BUS BMS, Color Control GX, Digital Multi.

Charger setup:




0 Likes 0 ·
1553270408976.png (96.9 KiB)
1553270538924.png (163.3 KiB)
1553270577661.png (49.4 KiB)
1553270622265.png (125.1 KiB)
boekel avatar image boekel ♦ eliott commented ·

ok, next thing to check: BMS


I -think- your charge voltage is so high your BMS stops the charging due to one cell being charged too high.

I don't know if you can see separate cell-voltages? this might give a clue.

Other way to try: lower absorbtion voltage to 56 V and see if this helps.





0 Likes 0 ·
eliott avatar image eliott boekel ♦ commented ·

Ok, thanks, I'll try that. I have no access to the cell data, I am remote now. But I can upload the config remotely I think. Should the new value be only temporary until the cells get balanced and should I increase it back?

0 Likes 0 ·
eliott avatar image eliott boekel ♦ commented ·

ok, it went into absorption. Do you think that the cells will equalise and I can turn it back to the recommended values?

0 Likes 0 ·
boekel avatar image boekel ♦ eliott commented ·

I don't know, I personally like to not charge above 3,45V per cell (55,2V) but I don't know if there is a minimum voltage to be reached to let balancing start (should be in the manual)

0 Likes 0 ·
Show more comments