Hello, just purchased a 100/30 Mppt victron charge controller. I have 2 200watt Rich solar panels. Can I use 3 200watt solar panels or only 2? Battery is 12 volt. Thank you
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hello, just purchased a 100/30 Mppt victron charge controller. I have 2 200watt Rich solar panels. Can I use 3 200watt solar panels or only 2? Battery is 12 volt. Thank you
There's a Victron calculator online which will do the calcs
As Kev has already pointed out, you’ll need to know the full specs of the panels to determine how many you can add to a given MPPT controller. For panels in series, the voltage values add together (take the Voc value on the panel label).
For panels in parallel, the current output adds together (take the Isc value on the panel label).
So long as the value of the Voc x the number of series connected panels is comfortably under the controllers voltage limit (100v in your case, so aim for around 90v maximum) that will be fine.
So long as the value of the Isc x the number of parallel connected panels is under the current rating of the MPPT (50a in your case), it will be fine*. For this you actually CAN go over that value, but the MPPT then won’t be protected against short circuit current and may be damaged if you make wrong connections whilst there is a current flowing. Other than that, if all is connected correctly, the power output will just be limited.
Additional resources still need to be added for this topic
25 People are following this question.