2100w of solar panels on 12v RV....12v system or 24v?

Hey all,

I could really use some help as I can’t seem to find a straight forward answer on the internet. I can give details if needed but to try to keep it simple here are the basics.

  • RV has 50a service and is 12v. I’d like to run all loads on batteries to avoid running the generator when possible.
  • Prewired solar wire pair from roof to basement....looks to be 8awg
  • 4s3p brings the solar numbers to 59v , 36a, and 2120w coming down from the solar.
  • 4x 200ah Ampertime batteries.

Question is: Do I stay with 12v or go to 24v with 24v to 12v converters for the 12v loads.

  • The system I have now does not charge the batteries quick enough to be useful. It’s a 12v Renogy system. I’m taking it out to upgrade to Victron.
  • I’ve already purchased many Victron components before solidifying a system. I will have to return or resell some items after the system is solidified.
  • I have a 12/3000/120 Multiplus and a 24/3000/120 Multiplus in hand. I can purchase an additional 24/3000/120 Multiplus for cheap if a split system stacked inverter/charger with autotransformer is recommended.
  • I have a 150/70-TR MPPT, Lynx Power In, ArgoFet battery isolator, 24/12-70a Orion Dc-Dc non isolated converter, smart shunt, smart battery protect, 2x battery balancers.

2nd question: If I stay with 12v should I go with the Multiplus II 2x 120v? If I go with 24v should I purchase the additional 24/3000/120 and autotransformer for split phase?


Thank you for your help. -Jaime in Cali

victron community
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Jaime Garcia

The 24v system would allow for the full use of the panels using the 150/70 for charging.

24v x 70A = 1680W (just using basic calculations). So for faster efficient use of the solar 24v system works better. (The batteries run at higher voltages so will use the 2000W)

The 24v system also allows for smaller battery cables and those kinds of considerations as the amp draw for the same power is smaller, so in a way cheaper and easier to install.

3000/24 is 125A on a single unit

3000/12 is 250A (and the system will have higher losses.)

2 |3000