question

toadhill avatar image
toadhill asked

Absorption Times

I have a smart solar 150/45. When I leave the cabin, I disconnect all loads. The controller will bulk normally, absorb for just a minute, and transition to float. Batteries typically do not go below 26.2 when I’m gone. Settings are adaptive, Tail Current 2 amps, BMV Tail is 2 percent, max duration:2:30. Is that normal.

battery charging
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
snoobler avatar image
snoobler answered ·

The behavior is normal for charges following:

1) Very shallow discharges where tail current is hit very quickly - regardless if fixed or adaptive is selected..

2) Shallow discharges where the adaptive algorithm varies the absorption time based on the depth of discharge.

https://www.victronenergy.com/upload/documents/Adaptive_charging_how_it_works.pdf

There could also be a configuration issue.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image
kevgermany answered ·

Sounds good.

Think of absorption as filling the hard to fill parts after bulk charging has finished. If there's no discharge, it was full to start with. So no absorption needed. Every day the charger turns on from sun. Goes immediately to bulk, battery is almost full (overnight self discharge is all) switches down to absorption. Battery says I'm full (tail current), switches down to float. If it stays in absorption unnecessarily, service life of the battery is shortened.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ahtrimble avatar image ahtrimble commented ·

I am trying really hard to understand "best" settings for my LifePO4 battery bank. I have 3 batteries, 630Ah (48v). I want to run my batteries 17% - 90% SOC to length their life cycle.

I am looking at setting my bulk charge voltage to 56v and absorption to 54v for 2 hrs and 0 tail current.

I can't figure out 2 things:

1) What should be my "float" setting?

2) What the heck exactly is "tail current"? I think I want it set to 0 to allow cell balancing. But I don't actually understand what tail current is.

I live in very sunny AZ so I want my MPPTs to keep running even after my batteries hit my target of 90%SOC so the MPPts can power my AC, etc. in the afternoon. But I am at a loss to really understand how I can accomplish my goals of not over/under charging my batteries while maintaining my MPPTs production and not drawing my batteries down when full sun is present.

Any thoughts, ideas, suggestions?

0 Likes 0 ·
snoobler avatar image snoobler ahtrimble commented ·

You can't target % SoC based on Voltage. LFP doesn't work that way.

56V will get you to very near 100%. Holding it for 2 hours with no tail current will absolutely, positively get you to 100% and beyond.

If your goal is to maximize cycle life in exchange for slower charge times, charge to 3.45V/cell with 2 hour fixed absorption and about 10A tail current. This should get you to about 95-98% SoC in a "low stress" fashion and help maximize cycle life while maximizing usable capacity at the expense of increased charge time.

1) Float at 3.375V/cell

2) Tail current is another charge termination criterion. Once absorption is hit, it is held, and the current tapers. If the current tapers to "tail current," then the MPPT drops to float.

Float is what will force the MPPT to hold the battery at 3.375V/cell and power loads with PV. If load causes battery voltage to drop, MPPT increases current to hold voltage. That current essentially is then fed directly to the load. When load is removed, voltage increases above float, so MPPT cuts current as needed to maintain float.

Recommend you get a smartshunt or BMV-712 and put it in a VE.Smart network with your MPPT. If you have a GX device with smartshunt or BMV, enable DVCC and enable SVS, SCS and if you have a temperature sensor, STS instead of the VE.Smart network.



1 Like 1 ·
ahtrimble avatar image ahtrimble snoobler commented ·
I tried to respond to your post...it is gone, lost, vanished.

I think I understand you, and I am grateful. I wish I could contact you directly to see if I got it right. This is a pivotal point to the system upgrade.


0 Likes 0 ·
ahtrimble avatar image ahtrimble snoobler commented ·

First Off...THANK YOU ! !

So "tail current" is the AC power amp draw on the system? Kinda like an "at rest" normal household amp draw? Or is it the DC amp draw on the battery in "at rest" normal household amp draw?

So the question is...is the tail current an AC or DC amp figure? I am thinking it is the AC loads that cause a DC amp draw. Now that makes sense if I am right.

Let me see if I get this, in absorption...my AC loads add up to 11a draw (tail current) and stays there (and my tail current setting is 10a) then my system will never drop to float. yes?

But, in absorption...my AC loads add up to 10a (tail current) or less (and my tail current setting is 10a) then my system will drop to float. yes?

And in float, if the AC loads cause the battery to noticeably discharge (DC voltage drop) then the float causes the MPPT to increase charging current (amps) to keep the battery at a steady SOC by powering the AC loads directly from the MPPT (if there is enough sun to do so)?

And reverses that process when the AC load drops and the MPPT float charging returns the battery to 100% SOC?

Please say I am right!! If I am right then I think it finally makes sense :)

--------------------------------------------------------------------------------------

I added a BMV-712 (w/shunt) last year, never got it working right. It will be removed from the upgraded system.

I have a GX Color Control that will stay with the upgraded system and be attached to my new Lynx Shunt.

I love Victron equipment!!!!! But dang, there is so much to learn about it...beyond all the normal solar stuff.



0 Likes 0 ·
snoobler avatar image
snoobler answered ·

No. Tail current is the charge current at when the absorption cycle stops, i.e., once absorption voltage is held to the point that the current drops to the tail current, that signals the charger to switch to float mode.

There's essentially no way for the MPPT to know what the AC current is, and it wouldn't have any meaning for it whatsoever.

Your description of float behavior with loads is accurate. Float is a target voltage for the MPPT or other charger to maintain. If anything (loads) causes the voltage to drop below float, current is added to maintain float.

Not sure why you couldn't get the BMV to work right. The biggest mistake folks make is if they don't follow the guidance. Many will set charged to 0.2V below FLOAT, which is fine for reliable AC chargers, but bad with solar. With Solar charging, this runs a common risk of false synchronizations where it jumps to 100% when it's at a lower state of charge. Simply enter your capacity, set charged voltage to 0.2V below your absorption voltage and set tail current of 6%.

I have no experience with the Lynx Shunt.

9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ahtrimble avatar image ahtrimble commented ·

The BMV was my fault. My version 1 system had no Victron equipment and was 15-year old technology, including the busbar layout and wiring. Then I added the BMV but its wiring needs were not compatible with the then current wiring...meaning I wired it wrong. I was going to rewire it correctly but I decided to just leave it be until the upgrade next month.

OK, I think I might have the tail current thing now. When the charge current in the absorption mode hits the tail current setting it drops into float. That means the absorption charging has done its job and the charge rate/current is dropping off due to lack of need.

OK, thank you for letting me know I finally understand the float mode. I hear folks saying float mode is not needed. But it sounds as if float is a pretty cool way to maintain a battery bank and keep loads powered up when there is enough sun to do so.

Now to the settings based on all of the above...I am looking at :

  • For a target of 95% of battery bank capacity I will set my 630ah battery bank to 598ah.
  • 56v for my bulk setting.
  • 54v for 2hrs for my absorption setting.
  • Tail current of 6% (36a for 598ah battery bank).
  • Float setting 53.8v.

Well, does that sound about right?

Your help has been amazing!! Feel free to send me an invoice :)

0 Likes 0 ·
Show more comments
ahtrimble avatar image
ahtrimble answered ·

Bingo!!! It all finally all makes sense.

Thank you guys a whole lot!

For some reason this just couldn't get into my head and make any sense.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sean-w avatar image
sean-w answered ·

Hi everyone

I’m also new to my Victron set up of a 100/50 mppt and a bmv

I have a battery bank of 530ah banner bull lead 12v


Should I keep the default settings in the mppt of 2A

And 4% tail current in the bmv


I am getting early syncs showing at least 4ah consumed still left but 100% so a little confusing

I

2 |3000