question

brucevanderbilt avatar image
brucevanderbilt asked

Lynx BMS error Code #205

My installation consists of 2 multiplus 12/3000/120 (in parallel), with Lynx Smart BMS, Cerbo GX, and 4x Victron Lithium 330ah batteries., and a Smart Solar 100/50. I've udpated the firmware on all these components.

I'm getting the following error code. I couldn't find anything about this error code in the Cerbo manual, the BMS manual, a google search, and a search in this community.

Does anyone know what this is?

lynx-alarm-205.jpg


error
lynx-alarm-205.jpg (40.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·
A fuse has blown.

@brucevanderbilt


screenshot-20220218-181456.jpg


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

brucevanderbilt avatar image brucevanderbilt commented ·

Thank you for this. At first, I was baffled because my fuse status appeared good in Victron Connect. When I checked them physically with a multimeter, I noticed I hadn't fully tightened down one fuse on the load side. Note, it's an unused fuse, hence the miss originally. Rookie error on my part. I believe that this must have caused an intermittent error. At least I hope that's what caused it.screenshot-20220219-063959.jpg

0 Likes 0 ·
Show more comments

Related Resources

Additional resources still need to be added for this topic