question

Klaus avatar image
Klaus asked

Lithium - mixing old and new batteries

Is it OK to expand a one year old set of two 330Ah Victron Lithiums Smarts with one new 330Ah Lithium Smart to upgrade to 990Ah capacity?


The older set has done somewhere between 50-100 cycles.

The installation is on a sailboat with discharging and charging currents typically less than 0.1C


If yes, after how many cycles/years would you no longer do an expansion in such a way?


Would the answer be any different if I do redundant load and discharge buses, i.e. every Lithium battery gets its own BMS + ATC Battery Protect + ATD Battery Protect?


Thank you!

Klaus.

Lithium Battery
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

Hi @Klaus Matzka,

I don't have a definitive answer. It depends for example on how deep were your discharges and typically also on internal cell resistance.

50-100 cycles down to 0% is different compared to discharge down to let's say 50%. In case of the latter the older battery is almost like new and I would give it a try by charging all batteries up 14.20V and let them balance. Then measure cell resistance (the 330Ah can be opened though not advisable!)

I'm guessing here but think that you have a GX device and either a VE.Bus BMS or a Lynx Smart BMS. I think it will not work with multiple BMS. Also, if you do have a GX device, it will only control the 'main' battery.


4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Klaus avatar image Klaus commented ·

Hi @Stefanie


Thank you for your fast and helpful response! :-)


I believe you are right: if the batteries are discharged lightly for a few dozen cycles it should be ok to add another battery of the same brand and model.


BTW, how does one measure the internal resistance? Just by measuring the resistance between the positive and negative poles?


Some more background: to keep the original question simple I have been pretending the system is already a year old. But I am actually currently planning the system now, and was looking back from the future… ;-)


The design:


I am planning to built a redundant load/charge bus, with one smallBMS per Lithium Smart Battery, plus one Smart Battery Protect for the charging side, and one for the loads side. No GX devices, no Lynx Smart BMS. I do not see the benefits of the more complex, more expensive and stand-by current sucking system. No need for remote monitoring. If I leave the boat for longer, I shut everything down completely, including BMSes, battery monitors, etc.


Why am I planning to install a dual bus system: to reduce the risk of one Lithium failing momentarily for whatever reason and taking down the whole DC system in a sudden leaving the boat without any energy. Imagine the auto-pilot (silently) failing while sailing single handedly during the night…


Back to the topic:


after some more research I came to the conclusion that adding a battery later might mean that I have to cope with batteries with different internal resistances.


Is this really a serious issue?


My guess: it would mean the new battery (of same brand/model/chemistry) is doing more work during load/discharge. Thus it would age faster than the older batteries. I conclude that would mean old and new batteries are coming closer in „age“ over time and then age further together.


Do you think this is a correct assessment?

0 Likes 0 ·
Show more comments
gn-ro avatar image
gn-ro answered ·

If the internal resistance of all batteries is similar, then you can use them in parallel with no problems. You can even use batteries with different capacities as long as they are of same technology (Li-Ion with Li-Ion or LifePO4 with LifePO4, etc.).

Remember, even a slight difference in voltage will overcharge the lower voltage one and discharge the higher voltage battery but this is not a problem if the batteries are using the same max and min voltage EXACTLY. The initial balance is not a problem, but try to add the newer battery close to the voltage of the "old" already running ones.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Klaus avatar image Klaus commented ·
Hi @gn_ro , thank you for your explanation! Very much appreciated!
0 Likes 0 ·
kurt-s avatar image kurt-s commented ·

When adding a second (new) Victron Smart LifePO4 battery in parallel with an older one, how does one be sure the batteries are using the same max and min voltage?

0 Likes 0 ·

Related Resources