question

Patrick Wardell avatar image
Patrick Wardell asked

Is anyone working on "AC Input 1" not displaying any power info from Multiplus-ii?

I have a new MH installation of a Multiplus-ii 2x 120 and cerbo gx and a touch 50.

It has been working fine and started buttoning everything up an decided to do a little load testing around 2kw with a 15A shorepower limit.

Now AC Input 1 and AC output 1 not displaying any power usage on touch 50 or vrm, even though everything seems to be working ok. Cerbo GX on firmware v2.80 and multiplus v4.90 to get rid of pll hum issue.

Hooked up MK3 and AC output shows power usage but AC Input 1 shows nothing.

Problem very similar to this link: Https://community.victronenergy.com/questions/89979/multiplus-ii-ac-input-suddenly-0-watt-on-gx-touch.html

Anyway, have done a lot of searching and issues like this seem to be a common problem, but can't seem to find a solution. I'm thinking maybe it's a hardware issue with the input current sensor.

Any help would be appreciated! Btw, it's not the data cable, hooking up the MK3 proved that.

Pat

Multiplus-IIcerbo gxinput current
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Vangelis Beligiannis avatar image
Vangelis Beligiannis answered ·

Hello. If you are using an external current sensor I cannot help you. If not there is a hardware problem with most of the new multiplus II. There is a problem in the current sense socket under the multi that causes ac input to be stuck on 0W. You need to just put a headphone jack in the socket 2-3 times and the problem is solved. I know it sounds stupid but it worked for me.

Hope this was the issue

9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jan Urbánek avatar image Jan Urbánek commented ·
MP2 48/5000/70 in 3 phase system L3 shows output only when grid not present after grid online the input and output says 0W. Take not connected 3.5mm jack whan i switch off the factory and several times plug in / out, now it works. By me it is issue in switching jack contact what comes loose and not switch to internal mesure circuit.
1 Like 1 ·
roblatour avatar image roblatour commented ·
This worked for me too - thanks!
1 Like 1 ·
pvpax avatar image pvpax commented ·

Just to add another datapoint:
My MP II 5k started oscillating between charging and discharging today, right after running seamlessly for 2 years and one month. Updating and restarting literally everything in the house didn't solve it - until I searched this great forum.
The headphone jack did the trick, system runs buttery smooth again.

To second @Patrick Wardell : It's a shame that such a common pennies-component plays havoc with an otherwise rock solid system. I hope Victron implements a more solid solution in future hardware revisions - i.e. something like the bridge for the external switch in pluggable screwterminals.

1 Like 1 ·
Patrick Wardell avatar image Patrick Wardell commented ·
Wow, this sounds very hopeful! I am using the internal current sensor. I do have an external current sensor that I am not using, but I will plug it in a few times and see if that fixes it. May also see if the external sensor works, sounds like they may be using the same circuit.


Seems they may be using the switch contact that are on certain 1/8in. audio jacks.

Will communicate results later today.

0 Likes 0 ·
Patrick Wardell avatar image Patrick Wardell commented ·

@Vangelis Beligiannis You are awesome!!!!!

Plugged and unplugged a few times and it worked. Just in time, I was getting ready to call for support.

This .05 cent part screwing up a multi-K$ setup sucks. You indicated this is common, but I did a lot of searching and could not find your solution anywhere. I would hope Victron would be all over this to get issue fixed.

Thanks again!!!

0 Likes 0 ·
Show more comments
Patrick Wardell avatar image Patrick Wardell commented ·

BTW, I did update the multiplus-ii to firmware v4.94 and it started displaying AC out 1 on the vrm before I tried the fix.

0 Likes 0 ·
Show more comments
simong avatar image simong commented ·
Thanks for that, worked a treat after spending hours going through settings.

Thanks again

0 Likes 0 ·
Alexandra avatar image
Alexandra answered ·

@Gyrogearloose

This was a fix in Venus OS 2.80

https://www.victronenergy.com/blog/2022/01/31/venus-os-v2-80/

See #6. So if it did not fix that then maybe a warranty claim/assessment is in order.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Patrick Wardell avatar image Patrick Wardell commented ·
Thanks... I was on v2.80, updated to v2.82 a couple of days ago. Reverted back to v2.80 just to see if v2.82 was problem. It has been working on pre and post v2.80.


I am thinking hardware issue, but hopping for something simple. I wonder if their current sensor has any inductive spike clamping to keep circuits from getting zapped.

1 Like 1 ·
ken-wagner avatar image
ken-wagner answered ·

We just had two Multiplus II running in parallel that had the same issue - reading zero input current when connected to shore power (Generator). We tried the plug and unplugging into the AC external current jack and it solved the issue. Thank you so much for your post. It is hard to believe that the connector opens up just sitting there, but it does.

2 |3000