AC In on Mp II limited


The total AC-In of a MP II 5000 will not go over 4600W. The AC in limit is set at 50A in the VE configure (+overrulled by GX) - the power assist is turned off. 2 Pictures attached where it can be seen that if the AC1-out increases, the charger will go down to the limit the total AC-in to 4600W.

Lowering the AC-in setting at the GX does limit the AC-in at the desired lower value. (just to check if the GX is actually overruling the VEconfigure setting)

1644616331892.png


1644616349474.png

Multiplus-II
1644616331892.png (36.1 KiB)
1644616349474.png (183.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Paul B avatar image
Paul B answered ·

Are you using ESS. If so check the grid set point

Otherwise a full discription of what's installed and the settings and Fw version


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

JohnC avatar image
JohnC answered ·

Hi @Xtend

You have ACIN labelled Generator. Maybe it's the genset limiting?

I have a 6kVA gen with 15A rated plugs, and that's about all it will supply from one plug, as it's probably designed to do.

Your ~207V isn't real healthy either, maybe on it's limit?

Load power factor can also influence this a little too.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

xtend avatar image
xtend answered ·

The 207V input did limit the MP II to give more power. This has been solved and the system is working fine now.