question

coreyzev avatar image
coreyzev asked

Charger says "Float" even though it's below Float voltage.

I really feel like I should be understanding this better than I am. I already read a bunch of posts here. I understand how "Absorption/Float/Bulk" works in the sense of charging from zero to 100. But I'm confused about it right now, as it discharges and then charges up again from 65%.

I'm doing an initial slow cycling of my batteries to get them ready. And I'm a little confused by what I'm seeing here. Currently sitting at ~53.5 volts, below the float voltage, and it's charging my battery at my specified rate. Why does it still say float? There's something about Float/Absorption/Bulk that I'm not getting. Wouldn't this be a bulk phase since the voltage is lower?


Mostly, I'm just confused why it says "float" when it's charging at the bulk charge rate.

Specs:

  • Victron Multiplus
  • Absorption Voltage: 56.8v
  • Float Voltage: 54.0v
  • Battery: LiFePO4
    • 300AH
    • 48v


273442225-3138547539691547-1247213391100470788-n.jpg

273585165-3138547836358184-3689570646867095556-n.jpg


EDIT:
The voltage was previously down to 52.15v, and still said "float". That doesnt seem right.

1644541296783.png


Multiplus-IIMPPT Controllersbattery chargingLithium Batteryfloat
5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

Look at the re bulk voltage.

Should be in the manual.

0 Likes 0 ·
coreyzev avatar image coreyzev klim8skeptic ♦ commented ·

I cannot find them in the manual or anywhere else aside from this from another question:

The Multiplus re-bulk voltage is as follows (depends if 'Lithium batteries' is the selected 'battery type' in the VEConfigure 'charger' tab):

  • Lithium: Re-bulk Voltage = Vfloat - 0.2V (max 13.5V) - for 12V system, multiply by 2 for 24V systems & by 4 for 48V systems

But i cant confirm it anywhere.

Mostly I'm just confused why it says float, but it's charging as if it's on bulk. This might be a bug.

0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ coreyzev commented ·
In VRM under the "advanced" tab, open up the widget for the "VE Bus System", and select "VE Bus State".

You will be able to see the charge state of the Multi going back to the start of the day.

0 Likes 0 ·
coreyzev avatar image coreyzev klim8skeptic ♦ commented ·

Yes I'm aware of that. You're still not really answering the question. Which is "why does it say float, while it's clearly charging at the full amps i set it at?"


Also, this is what it says in that visual, which doesnt help answer my question:
1644561917646.png

0 Likes 0 ·
1644561917646.png (11.2 KiB)
klim8skeptic avatar image klim8skeptic ♦ coreyzev commented ·
Well the charts are interesting at least..

You seem to have had a grid failure (genset ?) and the inverter has gone into AESS or search mode in the time that the inverter has synced to the input.

There is 1 period of power assist about when the power went off.

It looks like the multi has been switched off twice ??

the multi has not gone into bulk charge despite the voltage looking low enough to warrant a re bulk.

On the other hand, the voltage might have rebounded high enough that the multi did not start a re bulk charge. Thats my thinking.

What firmware are you running?

Why only an 8 amp charge current?

0 Likes 0 ·
3 Answers
JohnC avatar image
JohnC answered ·

Hi @coreyzev

Just guessing here, but that LiFePO4 preset you're using has a Repeated Absorption Time of 7 days. So if it's already had it's once-per-week 1 hour Abs, then it won't be targetting Abs when it does get some charge.

Rather it will be targetting Float, and I suspect then it won't show Bulk on the way there. Bulk is normally considered to be the transition stage on the way to Absorb.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

coreyzev avatar image coreyzev commented ·
That's the best guess I've seen so far. I just restarted the entire system after I let it go overnight and it charged it up until the float voltage and that's it. Everything says 100% SOC now, but when I turned it on it went back to bulk charging.


I'm gonna make a new post with the whole issue better explained and tag someone from Victron cause this is just silly now.


Clearly a bug.

0 Likes 0 ·
JohnC avatar image JohnC ♦ coreyzev commented ·
@coreyzev

If you've reset the Multi, then I'd expect it to attempt a new Abs period and show Bulk on the way there.

I suspect this isn't a bug, and is by design. Is it really so bad to see Float there for the rest of the week? At least it's signifying that your weekly cell-balance (Abs) is current and doesn't need repeating yet.

With Li's and a low charge rate you wouldn't see true Float target V achieved anyway until they're near 100% charged.

@Alexandra I don't think that 'Tail' issue applies here. Does it actually apply at all in a Multi (maybe in new firmware I haven't spotted yet)? :)

0 Likes 0 ·
Show more comments
Alexandra avatar image
Alexandra answered ·

@coreyzev

Try charging at a slightly higher amps.

Because the different stages of charging are both voltage and amperage based, the tail current and other requirements of the charge algorithm may be getting "mixed signals". A 4% tail current on a 300AH battery is 12Amps. You are charging under that.

I am guessing you have 16kwh bank easliy there it is charging at 400/500w is a bit strange on a large bank. That is 30ish hours at a high DOD.


A bmv would help alot as well if you want to keep the charge current lower as the system would then know its target AH to replace. But the tail current issue will still be an issue.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

goncalo avatar image
goncalo answered ·

Did you find what the problem was/how to solve it? I think I’m having a similar issue. The multi is always in float, never goes through bulk and absorption.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.