question

kai-gt avatar image
kai-gt asked

Current Transformer and parallel MultiPlus II

I just got my 2nd Multiplus II 3000/230/35. I plan to install both on the same Phase as Master und Slave Devices, Grid-Source is a 3 Phase Network. Just now a run an EM24 Meter, that works okay, but reacts slow at changes of large Loads.

I want to try the Current Transformer Clamp on the powered Phase near the EM24 as Reference for the Multiplus II and ESS, to speed up slow ESS Response Times. My Question is: Do i need two Current Transformers, one for each MP-II, or is one CT enough, connected with the Master MP-II.


Best Regards, Viele Grüße,

Kai

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

I have not done it myself but I suspect just one connected to the master should be fine

2 |3000