question

myshopsolaire avatar image
myshopsolaire asked

Port RX fonction gone on MPPT 100/50 ?

Hello,

Since the last update on Victron Connect app, the port RX fonction is gone on my SmartSolar MPPT 100/50. It's a problem because my VE BUS BMS can't remote my MPPT, throught the VE Direct non inverting remote ON/OFF cable, anymore.

SmartSolar MPPT firmware : v1.59
SmartSolar Interface firmware : v2.37
Bootloader : v1.15

Thanks,

Adrien

VictronConnectbug report
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

I am seeing what you have described. v1.59, v2.33, v1.14

RX port settings not accessible via Victron Connect v 5.27 or v 5.51. Demo on both versions gives access to RX port settings.

v1.59 firmware goes back to 03/08/2021 self install, or VC v5.48 07/10/2021.

Bluetooth firmware v2.37, bootloader v1.15 goes back to VC v5.52 03/01/2022.

0 Likes 0 ·
1 Answer
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @MyShopSolaire


Indeed the menu is gone, but the function remain there. The only possible RX function is the remote on/off, so there was no point in leaving the option to change it there.
That means that the remote on/off functionality will always be active for those products

We should probably make this more clear in VictronConnect.