3 Phase Quattro System with 2 x Inverters per Phase

Good Morning

I have an installation with 6 x Quattro 8000 Inverters in 3 Phase connection.

I have set it up using the VE Bus System Configurator and sent all settings. I have 0 errors and all seem to be working fine, however, I have blinking lights on the slave units. It jumps between the inverter on and Mains on green LED's.

Further, I have installed the ESS assistant on all units, however my Venus GX does not seem to see or recognize the assistants. I need to set up the ESS on the VENUS.

What could be the reason for this?

Is there another step to set up Master and Slave configurations for the 3 Phases?

Or am I missing something?


Nick

system design
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

The blinking on the slaves is normal.

Check again if the assistant is correctly added to the Quattros.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image
marekp answered ·

@Nick B1983

Blinking LED-s on slave unit is normal. It just tells you which one is a slave.

After answering all the questions during a assistant setup ("start assistant" button), you have to press "send settings" button in order to load assistant to your Quattro.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.