Hello,
Can someone shed a light on how would behave/respond the 3phase ESS system in case if one of the grid phases fails.
Thanks in advance,
Vyacheslav
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hello,
Can someone shed a light on how would behave/respond the 3phase ESS system in case if one of the grid phases fails.
Thanks in advance,
Vyacheslav
System will switch to inverting on all phases.
If you want your system to react to missing grid on phase by phase basis, You can set each phase as a separate 1-phase system. You will not be able to use a 3-phase equipment but all your 1-phase equipment would work.
It doesn't matter if you use ESS or not.
If you setup 3 MultiPlus (or Quattro) to run together as 3-phase system, they always switch to inverter mode if one of the phases fails.
Thanks, Matthias, I can explain why I was confused a bit. If you open a recent Victron's blog page https://www.victronenergy.com/blog/2021/12/17/electric-vehicle-charging-that-comes-to-you/ on the GX Touch Screen you can see the only one phase available as power source and three phases are operating, on top of that it is in Power-Assist mode. That's definitely not an ESS setup, although operating as a 3phase system.
Thanks again,
Vyacheslav
In such system you should also be able to use a different input on each MultiPlus but if I'm correct it will only use one input at a time. You can't connect a 3-phase grid to the input and use all three phases together. But I'm not 100% sure about that.
41 People are following this question.