question

andyc avatar image
andyc asked

multiplus conform to g99?

hello

does the multiplus 5000 48v conform to g99? if so where can i find certificate?

(not multiplus 2) thank you


MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
wkirby avatar image
wkirby answered ·

If there is no certificate listed for that device then I would say that it either does not conform or it has not been submitted for verification.
Perhaps it is known that the older devices would not comply to G99 so submitting them for testing would be a waste of resources.

There are several other parameters to which the older devices may not comply. One that springs to mind is that the older devices only have a single relay for disconnection, so they may have conformed to G59 but G99 requires a double relay disconnection (two separate relay contacts in series) for additional disconnection assurance.

In case you are unaware, the certificates are listed here:
https://www.victronenergy.com/support-and-downloads/certificates

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

bladerunnervf avatar image
bladerunnervf answered ·

Yes.

https://www.ena-eng.org/gen-ttr/TTf1l3s/VICEN_02689_230331012607.pdf

you can search from ENA home page

https://www.ena-eng.org/gen-ttr/index?Action=Home


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Craig Chamberlain avatar image Craig Chamberlain commented ·
That’s the Multiplus-II, the OP was asking about the original Multiplus
0 Likes 0 ·