hello
does the multiplus 5000 48v conform to g99? if so where can i find certificate?
(not multiplus 2) thank you
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
hello
does the multiplus 5000 48v conform to g99? if so where can i find certificate?
(not multiplus 2) thank you
If there is no certificate listed for that device then I would say that it either does not conform or it has not been submitted for verification.
Perhaps it is known that the older devices would not comply to G99 so submitting them for testing would be a waste of resources.
There are several other parameters to which the older devices may not comply. One that springs to mind is that the older devices only have a single relay for disconnection, so they may have conformed to G59 but G99 requires a double relay disconnection (two separate relay contacts in series) for additional disconnection assurance.
In case you are unaware, the certificates are listed here:
https://www.victronenergy.com/support-and-downloads/certificates
Yes.
https://www.ena-eng.org/gen-ttr/TTf1l3s/VICEN_02689_230331012607.pdf
you can search from ENA home page
https://www.ena-eng.org/gen-ttr/index?Action=Home