cerbo GX power from Orion -TR not visible in total calculation

on touch 50 display only the BMV712 current results (totals) are visible and not the power consumed / delivered by multiplus 12/500 and the calculated difference delivered from orion -TR smart.

expected to have visible:

currents to from multiplus inverter/charger

and from BMV717 the battery current

The difference would be then the current out of the orion-TR

Is this a correct assumption, also the item DC load is not visible on touch 50.

cerbo gx
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kuperusron avatar image kuperusron commented ·
Problem solved, use selection system setup and select Has DC System then additional power feed is visible.
0 Likes 0 ·
1 Answer
bathnm avatar image
bathnm answered ·

Have you turned on "Has DC System" under System Setup.

This is a calculated value, which mill show the difference between battery, inverter (DC) and solar through a calculation.