Limit the charging power of the MPPT and MultiPlus, commander par BMS CAN

Hello,

I currently have a problem with my BMS CAN (LiFePo4) , MPPT and MultiPlus.


In the case where the BMS limits the charging current to eg 2A the MultiPlus no longer charges, but the MPPT always charges to the maximum of it's capacity.

But if the MultiPlus is OFF, the intensity information is 2A on the MPPT.


I would like the excess power of the MPPT to be reinjected to the network.

The MPPT is well controlled by the BMS.


Load current setpoint of BMS CAN.


The injection of the excess power of the MPPT is active.


Is it possible to do this function, if yes what is the configuration?


Bonjour,

J’ai actuellement un problème avec mon BMS CAN, le MPPT et le MultiPlus.

Dans le cas où le BMS limite le courant de charge a par exemple 2A le MultiPlus ne charge plus, mais le MPPT charge toujours au maximum de c’est capacité.

Mais si le MultiPlus est sur OFF, l’information d’intensité est bien de 2A sur le MPPT.


Je voudrais que la puissance excédentaire du MPPT soit réinjecter sur le réseau.

Le MPPT est bien contrôlé par le BMS.

L’injection de la puissance excédentaire du MPPT est active.


Est-il possible de faire cette fonction, si oui quelle est la configuration ?

MPPT ControllersMultiPlus Quattro Inverter ChargerLithium BatteryBMS
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Are you saying that the system is performing as you want it to and as you expect it when the Multi is on.

But does not perform as you want or expect when the multi is off?

Or it does not perform how you want or expect in either state?

0 Likes 0 ·
Show more comments
mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ commented ·

Hi; just a small remark: I’ve moved your question to the Mods Space.


See here for details: https://community.victronenergy.com/questions/10881/launching-the-mods-space-a-new-section-on-communit.html

0 Likes 0 ·
1 Answer
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Limiting the mppt on current; as per received by the BMS; but then still allow the excess PV to go to the loads via the inverter doesn’t work.


The solution is to not limit in current but lower the voltage; which has the desired result.


Note that we don’t officially support all BMS-es. The ones tested and supported are listed here, on our Battery Compatibility Page.

2 |3000